Also these systems do not run 100% of the time. If the system is low on charge, the low pressure switch shuts the compressor off, so that will not cause it to freeze up. Over charging WILL cause it to freeze up because the pressures will stay to high, and it won't cycle off when it should. Which low pressure switch did you put in it? There is one for R-12, and one for R-134A. The 2 refrigerants have different operating charicteristics, sort of like R-22 vs R-410a. R-134A is a higher pressure refrigerant than R-12, but 134 actually needs to shut off at a slightly lower pressure and come back on at a higher pressure than R-12. R-134 is not as dense, hence why you charge the system to roughly 75-80% of the weight with R-134A as you do R-12, but even with the lower charge volume, it runs higher pressures until the low side gets close to freezing at which point it dips below R-12 pressures. I would put in a R-134 retrofit condenser, R-134A pressure switch, then recharge the system to roughly 85% of the R-12 charge(the larger condenser will take more charge). It will lower your high side pressure allowing it to more efficently transfer heat through the evap and increase your system charge.